Hi,

when heating my frementer, Brewblx will control a 220V (2.3A) heating element. Cooling is a 12V solenoid.

My questions is if for the heating side I have to connect all six of the pins (3x -, 3x +) with my SSR? Is it OK when heating runs with external 12V supply too (because of the 12V solenoid I need external supply?), or do I need seperate modules for heating and cooling, one 5V the other 12V?

Thanks

Patrick

If the heating element is controlled by SSR, the control wire on the SSR will not have a 2.3A load. You can use 1x + / 1x - here.

If the heating SSR is rated for >12V on the control side (ours are), you can use the same GPIO module for both heating and cooling.

Thanks! So, 1A and 1x + and 1x - is enough for the control wire on the heater side.
The SSR input is 3~32DCV, so I should be fine with 12V external power for both.