As you can see for the first 3 days of this graph (and the previous brew) it maintained a reasonably stable temp in my beer but starting on the 10th something weird is happening.
As far as I’m aware no one had touched the fridge in a week.
I did think of that and did an upgrade last friday (15th) but it still appears to be happening. I was interstate over the weekend and this is what greeted me this morning.
Here is the Cool PID Graph. Trying to track down Kp.
No thermowell. I’m using a glass Carboy and I haven’t figured out how to use a thermowell without cracking the glass
The temp probe is in the wort.
Ti (time constant of the integrator) is the time it takes for the integral to grow (with the same amount as what the proportional part is).
The purpose of the integrator is to correct long term errors. It should therefore be much slower than normal process response times.
If you set it to 1 minute, it comes down to this (simplified):
Proportional output is set to 10% due to a 0.1 degree error.
The integrator says 'hey, we have been cooling for a minute already and are still not on target! Better bump that to 20%! And it will continue to increase by 10% every minute.
So the beer is given no time to respond to cooling and the integrator ramps up the output to 100% much too fast.
Ok now I’ve broken something with the current ferment.
As you can see from the profile it should have bumped the temp up but hasn’t.
Essentially the red line (target temp) has moved but the orange line (actual temp) hasn’t moved.
I’ve had a quick look but can’t figure it out. Any clues would be greatly appreciated.